hi, I installed circuit breaker 50amp with 6 AWG, when I put 100% of the charged cable and the socket gets very hot, 50% does not happen the same, what can it be? thank you
 

·
Premium Member
Joined
·
221 Posts
Was it professionally installed or have you had a certified electrician test and inspect everything? Could be a wiring issue, bad plug, or maybe even an issue with the charger itself.

And I assume this is the Audi charger? Do you have access to another charger? If wiring is OK, talk to the dealer, see of they can replace the charger.
 