Anyone else receive this? Pretty alarming.
The issue with a 60A breaker is not the Emopria EVSE, it's the NEMA 14-50 in between the breaker and the EVSE. Breaker is supposed to protect the circuit, meaning the wiring and the outlet. Even if the wiring is 60A capable, but the outlet is 50A capable, the breaker has to be 50A, and EVSE has to be set to draw no more than 40A (80% of the circuit max). If you remove the outlet and hardwire the EVSE, you can use 60A breaker and set the EVSE to 48A max.The Emporia manual says it “requires a dual-pole, dedicated breaker at 60A+ for a 48A charge or 50A+ for a 40A charge.” Since it’s saying 50A+ why wouldn’t 60A work?
And then packrats will gnaw the charger wire and burn your house down anyway.We purposely had a hardwired EV charger (Wallbox Pulsar+) added to the OUTSIDE of our home to facilitate charging in the driveway. Not trusting large battery packs inside the home.![]()
As long as everything is working as it should, there shouldn't be a problem. The electrical codes are developed to give protection even when things don't operate as they should.I now understand and I don’t think this is an issue with my setup. My EVSE Emporia charger only outputs 40A when it is plugged in. It won’t output 48A unless it is hardwired (it’s built that way). If I’m understanding this correctly, as long as it only outputs 40A there shouldn’t be a problem, is that right?
GFCI is actually meant to protect between the NEMA 14-50 outlet and the EVSE, against things like touching the plug prongs by accident, or having a longer wire from the outlet to the EVSE cut by accident (since it is exposed and not mounted to anything as it is a plugin). If it is in the breaker, it protects the line between the breaker and the outlet too, but that is already supposed to be protected from ground faults by being hardwired. This is why a NEMA 14-50 GCFI outlet instead of the breaker would also satisfy the code GCFI requirement, just like for kitchen or bathroom outlets you can use either a GFCI breaker or GFCI outlets - the cabling between the breaker and hardwired outlet does not need GFCI protection.Based on your explanation, our GFCI installed breaker protects only the section of the circuit up to the Nema 14-50. As stated by Getmoving, this requirement would not be applicable to a direct wire charger. Hence, for a plug-in charger, we would require the GFCI, which is currently mandatory for all installations, irrespective of the manufacturer's specifications, unless otherwise mentioned in the installation requirements.
That is part of the SAE J1772 specification which applies to all J1772 EVSE's. The spec is not free (J1772_201710: SAE Electric Vehicle and Plug in Hybrid Electric Vehicle Conductive Charge Coupler - SAE International), but if you Google it you can find plenty of documentation/presentations talking about it. To reiterate, this GFCI only protects the cable between the EVSE and the car, it will not trip if you drive over a cable between the outlet and the EVSE, damage that cable, then touch it and get electrocuted (that is what the GFCI in the breaker or outlet is supposed to protect against).I would appreciate it if you could provide me with some documented evidence or the owner's manual showcasing that the Audi 40amp travel charger includes a GFCI and the specific installation parameters prior to the recall.
If the box was rated for 60A continuous, and if it was behind a 60A breaker, and the wiring was rated for 60A continuous, that means something failed its rating. Either:The box that was melted had a continuous load rating of 60 amps, which is why I find it surprising that it melted so quickly.
Again, what the manual tells you here only applies if you hardwire. You cannot connect a NEMA 14-50 outlet to a 60A breaker, since NEMA 14-50 outlets or plugs are only rated for 50A (40A sustained). The outlet is your weak point (again, assuming the wiring is 60A capable, given that the installer connected a 60A breaker to a NEMA 14-50, I am starting to doubt your installers expertise). If you want to charge at 48A, I would:The Emporia manual says it “requires a dual-pole, dedicated breaker at 60A+ for a 48A charge or 50A+ for a 40A charge.” Since it’s saying 50A+ why wouldn’t 60A work?
If your Emporia came with the NEMA 14-50, then it assumes it's on a 50A circuit, hence it only draws 40A. Your breaker should be 50A not 60A for this setup. Wiring needs to be 50A+ capable.I now understand and I don’t think this is an issue with my setup. My EVSE Emporia charger only outputs 40A when it is plugged in. It won’t output 48A unless it is hardwired (it’s built that way). If I’m understanding this correctly, as long as it only outputs 40A there shouldn’t be a problem, is that right?
The Emporia lets you pick what the circuit is, i.e., either 50A pr 60A. The manual tells you to select 50A if it is plugged in, even if it's a 60A breaker. This way it will only draw 40A. I've now looked into it a bit more and it appears irrelevant if the breaker is 60A even with a 14-50 outlet as long as you tell Emporia that it's 50A, i.e., the charger actually contemplates a 14-50 plug with a 60A breaker.If your Emporia came with the NEMA 14-50, then it assumes it's on a 50A circuit, hence it only draws 40A. Your breaker should be 50A not 60A for this setup. Wiring needs to be 50A+ capable.
All due respect this is not correct. There is a specific option in the Emporia charger where you tell the charger the size of the breaker and based on what you say, the charger outputs either 40A or 48A.The Charging unit has no idea what size the breaker is. It's up to you to be smart, and size the breaker accordingly, or dumb, and use an over-sized breaker.
But YOU are telling that to the charger. There is no way for the charger to sense that, so it is a far from foolproof method,.All due respect this is not correct. There is a specific option in the Emporia charger where you tell the charger the size of the breaker and based on what you say, the charger outputs either 40A or 48A.
A 60A feeding a NEMA 14-50 will not pass electrical inspections in most places. You might never see a problem with your setup, but you can have problems should the car be faulty/break and draw more current than advertised, should the EVSE be faulty/break and advertise the wrong current. I've been driving EVs for over a decade, 6 EVs to date (2 at a time), have yet to see a car draw more (though all cars were decently new) but have seen one EVSE break and advertise the wrong values. If that happens, the EV or EVSE manufacturer will say that your breaker was supposed to be properly sized and protect your circuit even if their product malfunctions, and they'd be right - this is supposed to be a swiss-cheese model where more than one protection needs to fail for bad things to happen. Insurance company will probably agree as that will save them having to pay for your damages, and if your house catches on fire and damages neighboring properties, those owners will likely sue you too. If this was a licensed electrician you paid for a complate install, who got the required permit and passed inspection, it will be on him and the inspector, but if you paid some guy under the table, it's on you. You using a too large breaker is similar to not using a breaker at all and just counting on main home breaker to pop should there be a short, but still risking a fire if there is too much current being drawn.The Emporia lets you pick what the circuit is, i.e., either 50A pr 60A. The manual tells you to select 50A if it is plugged in, even if it's a 60A breaker. This way it will only draw 40A. I've now looked into it a bit more and it appears irrelevant if the breaker is 60A even with a 14-50 outlet as long as you tell Emporia that it's 50A, i.e., the charger actually contemplates a 14-50 plug with a 60A breaker.
ChargePoint does it the same way. It’s just their way of applying the 80% “de-rating” of the circuit for continuous load. I found it a bit confusing, actually.All due respect this is not correct. There is a specific option in the Emporia charger where you tell the charger the size of the breaker and based on what you say, the charger outputs either 40A or 48A.
Well, they do know because either:The Charging unit has no idea what size the breaker is.
But, again, that is only because someone set things up in advance. You could go and change the breaker to whatever you liked and the EVSE would not have a clue.Well, they do know because either:
- Installer told the EVSE of the circuit size by setting appropriate dip switch or software setting at installation time
- The plug pigtail has signaling which tells the EVSE what plug is being used, and EVSE looks up maximum current for said plug - Audi charger does this, as to Tesla Mobile Connectors and other vendors of portable/pluggable EVSEs.
Correct. EVSE does not detect the breaker size. Some EVSE detect the plug type, and electrical code mandates the breaker size for a matching outlet. So an EVSE with a NEMA 14-50 plug will draw max 40A assuming 50A circuit, it plugs into a NEMA 14-50 outlet, and that outlet must be protected by a 50A breaker.But, again, that is only because someone set things up in advance. You could go and change the breaker to whatever you liked and the EVSE would not have a clue.
Actually a 40A circuit connected to a NEMA 14-50 is a bad idea. It has actually started fires in the past (2013 Toronto, Canada IIRC), causing Tesla to change their Mobile Connectors to 32A max (initially they did it via software update, then redesigned the Mobile Connectors to be only 32A). Here is why this is bad:My situation is the opposite. When the electrician installed my 50A house 14-50 plug circuit for me to use with Audi EVSE, he installed a 40A breaker. He said that, even though the house circuit had to be increased due to "continuous use", the breaker still should not exceed the rating of the device on the circuit (40A EVSE). Made sense to me--after all, the risk from "continuous use" is not that more amps are suddenly going to start flowing, it is that the circuit might warm up too much over time. I've used it for over 4 years with no problem.